On Thu,1/15/2015 11:55 AM, Bill W7KXB wrote:
> Ken: Better read up on issues that arise with multiple ground rods for home AC grounding. I don't have the info at hand but you'll find it on the www
The only "issues" that arise is failing to bond them together. The
simple rule -- you can have as many earth electrodes as you like, but
they MUST be bonded together, and to the power system safety ground bus
at the service entrance.
http://k9yc.com/GroundingAndAudio.pdf
73, Jim K9YC