Agreed!
Roger (K8RI)
On 10/4/2016 Tuesday 3:50 PM, Jim Brown wrote:
> Not quite. What must happen at the "Main Panel" is the bond between
> Neutral and Equipment Ground. That bond MUST be done where power
> enters the building, and it MUST be the ONLY connection between
> Neutral and Ground anywhere in the system. There must also be an Earth
> Connection (that is, a driven rod) at that point. ANY building can
> have as many EARTH connections as you like, and they can be connected
> to the "Green Wire" ANYWHERE you like, but they MUST all be bonded
> together.
>
> "Equipment Ground" in the context of power systems is the steel
> enclosures of electrical panels, and of the "Green Wire" throughout
> the building.
>
> 73, Jim K9YC
>
> On Tue,10/4/2016 12:28 PM, Roger (K8RI) wrote:
>> I think we're caught in semantics and interpretations. Jim (K9YC) has
>> the correct interpretation, BUT as he says, it' the GROUNDS that are
>> all tied together.
>> I believe Panels and sub panels are grounded ONLY at the main panel.
>> Sub panels have their grounds run to the main panel which is the only
>> ground for the panels
---