[TowerTalk] Naive question about lightning protection
Tom Rauch
W8JI@contesting.com
Mon, 7 Aug 2000 10:17:34 -0400
Hi Sylvan,
> Over the past couple of weeks there has been some interesting discussion
> about towers and lightning protection. However, as I recall nothing
> specific was mentioned about the difference between protecting a insulated
> versus and uninsulated tower. Is there a difference in the approach? Is an
> ungrounded insulated tower more or less prone to lightning strikes?
>
> tnx
> sylvan
Most insulated towers are used with large radial systems. I have
two large insulated towers, the shortest is 200 ft and the other is
over 300 feet tall.
What I do is drive a short copper pipe near each tower leg. I bond
the pipes into the buried radial systems terminating buss.
I bend the pipes so they parallel the legs for a short distance, and
set the gap just beyond what the transmitter will arc.
The coaxial and lighting leads from the towers go though large
single-layer air-insulated coils that retard the lightning and isolate
the leads for RF (so I can feed the towers as verticals). The
feedwires that feed the towers have a large single turn loop that
retards lightning and a gap on the network side.
Insulated towers are no more likely to get hit than grounded towers.
How they are grounded makes no difference in how attractive they
are as lightning targets, although it certainly can affect the damage
that occurs after a strike.
73, Tom W8JI