[TowerTalk] Pull rope twisted in conduit
kk9a at arrl.net
kk9a at arrl.net
Fri Aug 1 17:39:52 EDT 2003
I have a 350 foot - 4" diameter conduit that I have fished wires through
several times. I have many many wires in the conduit and I would never
consider pulling them all out just to add additional wires. I install an
extra 12ga electrical wire and use that for pulling future wires. When I do
add wires, I dig up the end by the tower and remove the fittings so I can
pull straight out of the pipe. If you can do that at both ends you'll
really benefit as angle fittings (even 45 degree ones) add a lot of
resistance. Also use plenty of pull lubricant.
73,
John
----- Original Message -----
From: "Jim Idelson" <k1ir at designet.com>
To: "TowerTalk Post" <towertalk at contesting.com>
Sent: Friday, August 01, 2003 14:51
Subject: [TowerTalk] Pull rope twisted in conduit
Hi everybody,
I pulled a couple of small cables through my 100 foot 3" conduit that goes
from
the house to the tower. This time it was extremely difficult. I can't even
pull
the cable another inch. I'm lucky that it's just sticking out the other
end.
Seems like the pull rope is twisted around some of the cables; and getting
worse every time I pull something else through. What's the best way to deal
with this?
A. Start using cable pull lubricant and don't wory about it?
B. Fish a new pull rope through the conduit? If this is the right answer,
what's the right way to do it? This sounds like the proper thing to do, if I
can figure out how.
73!
Jim Idelson K1IR
email k1ir at designet.com
web http://www.designet.com/k1ir
_______________________________________________
See: http://www.mscomputer.com for "Self Supporting Towers", "Wireless
Weather Stations", and lot's more. Call Toll Free, 1-800-333-9041 with any
questions and ask for Sherman, W2FLA.
_______________________________________________
TowerTalk mailing list
TowerTalk at contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk
More information about the TowerTalk
mailing list