On Sat, 15 Jan 2005 16:08:55 -0800, Jim Lux wrote:
>the neutral and electrical safety
>ground are supposed to be bonded at only one point, 
YES.  (All caps for emphasis) 
>and that's the service entrance.  
In a home, YES. In a building where there may be a transformer to establish a 
new system, the NEW neutral must be bonded to ground close to that 
transformer.AND all grounds must be bonded together.  
>You might be able to rebond the neutral at a subpanel, but I'm not sure.
NO, NO, NO, NO!  :)  You were right the first time -- once, and only once, per 
system. 
>Perhaps a better approach is to bond your buss to the building grounding
>system?
ABSOLUTELY! 
Jim Brown  K9YC
    
    