At 03:12 PM 1/21/2005, ny6dx at netscape.net wrote:
>Bud,
> I think there is more here than meets the eye.A gfi breaker is not rf
> sensitive,its meerly a current transformer that monitors the current
> relation between the 120volt lead and the return on the nuetral leg.Only
> an inbalance in this flow would cause such a failure.
There's a fairly sensitive amplifier to measure the differential current
(using a transformer with both Line and Neutral running through the core,
along with a sense winding). That amplifier or the detection circuitry,
might be RF sensitive.
In fact, the Leviton GFCI brochure
(http://www.leviton.com/pdfs/gfci/GFCI_Brochure.pdf) mentions "increased
noise immmunity: Higher resistance to electrical noise (EMI/RFI) to help
reduce nuisance tripping" as required by UL starting 1 Jan 2003.
That brochure has some nifty looking devices that might be useful.. GFCIs
with pilot lights, for instance.
There's also some description of why GFCIs for cord sets (the field day
sort of application) are different than for normal receptacles. It has to
do with a live hot leg with an open neutral on the line side. The tripping
mechanism won't have any power to operate.
Here's a typical chip used in these things:
http://www.fairchildsemi.com/ds/RV%2FRV4141A.pdf
http://www.fairchildsemi.com/ds/KA%2FKA2807.pdf
The latter requires all of 5 microamps to fire... It's easy to see how RFI
could get in there and trip it. Don't forget that these are a cost
sensitive device: the mfr's not going to put any parts or filtering in
there unless absolutely needed (viz. the recent UL rule change).