[TowerTalk] CQ article error(?)
Bill Aycock
baycock at direcway.com
Fri Oct 7 10:59:05 EDT 2005
But, Gary- he has the ground NOT connected to the neutral at the service
disconnect point.
Bill
Gary Schafer wrote:
>
>
> Bill Aycock wrote:
>
>> The regular article, "Math's Notes" in CQ in the October issue is on
>> the subject of wiring safety, but appears to have a serious flaw
>> concerning the concept of "single Point Ground" as currently used by
>> most Hams, and as required by my local power company.
>> In the article, the neutral and the earth ground are only connected
>> through earth at the panel end and the transformer end of the service.
>> Comment? Am I wrong, here?
>> Bill-W4BSG
>>
>
> Ground is to be connected to neutral only at the main service
> disconnect point. The power company also grounds neutral at the
> transformer.
>
> 73
> Gary K4FMX
>
>
>
>
>
>
--
Bill Aycock W4BSG
Woodville, Alabama