[TowerTalk] CQ article error(?)

Bill Aycock baycock at direcway.com
Fri Oct 7 11:53:03 EDT 2005


Gary- when you indicate a quote, you MUST be sure to use the real quote. 
You severely edited my statement and changed the meaning. What I SAID, 
(AND THIS IS A REAL QUOTE, COPIED FROM MY POST) WAS:

>In the article, the neutral and the earth ground are only connected 
>through earth at the panel end and the transformer end of the service.
>
The "through earth" makes MUCH difference. There is no wire or metal 
connection- only earth, between two rods or a rod and a pipe. This is 
not an SPG.
Bill


Gary Schafer wrote:

> Maybe I am misunderstanding what you are saying the article says? I 
> don't have the article.
>
> You said: "In the article the neutral and ground are only connected at 
> the panel end and the transformer end".
>
> That is the correct way to do it provided the "panel" is the main 
> service disconnect. If the panel is a sub panel or the main disconnect 
> is located at the meter or somewhere else away from the "panel" then 
> the neutral ground connection should be at the main disconnect only 
> and not at the "panel".
>
> So which way is the article saying to do it??
>
> 73
> Gary  K4FMX
>
> Bill Aycock wrote:
>
>> But, Gary- he has the ground NOT connected to the neutral at the 
>> service disconnect point.
>> Bill
>>
>> Gary Schafer wrote:
>>
>>>
>>>
>>> Bill Aycock wrote:
>>>
>>>> The regular article, "Math's Notes" in CQ in the October issue is 
>>>> on the subject of wiring safety, but appears to have a serious flaw 
>>>> concerning the concept of "single Point Ground" as currently used 
>>>> by most Hams, and as required by my local power company.
>>>> In the article, the neutral and the earth ground are only connected 
>>>> through earth at the panel end and the transformer end of the service.
>>>> Comment? Am I wrong, here?
>>>> Bill-W4BSG
>>>>
>>>
>>> Ground is to be connected to neutral only at the main service 
>>> disconnect point. The power company also grounds neutral at the 
>>> transformer.
>>>
>>> 73
>>> Gary  K4FMX
>>>
>>>
>>>
>>>
>>>
>>>
>>
>
>
>
>
>

-- 
Bill Aycock W4BSG
Woodville, Alabama




More information about the TowerTalk mailing list