Gary- see inserted comments
Gary Schafer wrote:
> Sorry bill, I was trying to make a clearer statement out of what you 
> were quoting from the article. If that is exactly What they are saying 
> then the article doesn't make sense. Maybe you are reading into it 
> something that they are not trying to convey?
It is a diagram and it is very clear, even if you have to trace it. 
There is no metallic conductor between the transformer neutral and the 
house earth ground
> I read it as saying that neutral is only connected TO earth at the 
> panel and the transformer. Maybe I am reading something into it?
Thats right, but it leaves out part of what is said. The earth 
connections ARE only at the two ends, but good practice and my power 
company requires a metallic path, as well.
>
> As far as single point grounding is concerned as hams refer to it, 
> This really has nothing to do with it. The idea with the power line 
> neutral and ground is to never have the ground carry any neutral current.
I disagree- the SPG and household wiring are inseparable because all the 
conductors in the house are related to ground by the neutral and safety 
ground wires.
>
> With single point grounding for the antenna / power system the idea is 
> to not have ground paths through any equipment to ground.
>
> 73
> Gary  K4FMX
>
>
> Bill Aycock wrote:
>
>> Gary- when you indicate a quote, you MUST be sure to use the real 
>> quote. You severely edited my statement and changed the meaning. What 
>> I SAID, (AND THIS IS A REAL QUOTE, COPIED FROM MY POST) WAS:
>>
>>> In the article, the neutral and the earth ground are only connected 
>>> through earth at the panel end and the transformer end of the service.
>>>
>> The "through earth" makes MUCH difference. There is no wire or metal 
>> connection- only earth, between two rods or a rod and a pipe. This is 
>> not an SPG.
>> Bill
>>
>>
>> Gary Schafer wrote:
>>
>>> Maybe I am misunderstanding what you are saying the article says? I 
>>> don't have the article.
>>>
>>> You said: "In the article the neutral and ground are only connected 
>>> at the panel end and the transformer end".
>>>
>>> That is the correct way to do it provided the "panel" is the main 
>>> service disconnect. If the panel is a sub panel or the main 
>>> disconnect is located at the meter or somewhere else away from the 
>>> "panel" then the neutral ground connection should be at the main 
>>> disconnect only and not at the "panel".
>>>
>>> So which way is the article saying to do it??
>>>
>>> 73
>>> Gary  K4FMX
>>>
>>> Bill Aycock wrote:
>>>
>>>> But, Gary- he has the ground NOT connected to the neutral at the 
>>>> service disconnect point.
>>>> Bill
>>>>
>>>> Gary Schafer wrote:
>>>>
>>>>>
>>>>>
>>>>> Bill Aycock wrote:
>>>>>
>>>>>> The regular article, "Math's Notes" in CQ in the October issue is 
>>>>>> on the subject of wiring safety, but appears to have a serious 
>>>>>> flaw concerning the concept of "single Point Ground" as currently 
>>>>>> used by most Hams, and as required by my local power company.
>>>>>> In the article, the neutral and the earth ground are only 
>>>>>> connected through earth at the panel end and the transformer end 
>>>>>> of the service.
>>>>>> Comment? Am I wrong, here?
>>>>>> Bill-W4BSG
>>>>>>
>>>>>
>>>>> Ground is to be connected to neutral only at the main service 
>>>>> disconnect point. The power company also grounds neutral at the 
>>>>> transformer.
>>>>>
>>>>> 73
>>>>> Gary  K4FMX
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>
>>>
>>>
>>>
>>>
>>>
>>
>
>
>
>
>
-- 
Bill Aycock W4BSG
Woodville, Alabama
    
    
More information about the TowerTalk