[TowerTalk] CQ article error(?)
Bill Aycock
baycock at direcway.com
Fri Oct 7 15:03:32 EDT 2005
No- no added wire. The "metallic conductor" I refer to IS the neutral
wire, but there is an added bond from that to the earth ground rod
within the panel.
Significantly, ALL panels I have ever seen have this "Bonding
connection" between the green wire blocks and the neutral blocks.
Neither the green or the neutral is switched.
TexasRF at aol.com wrote:
> Bill, do you mean a metallic conductor in addition to the normal third
> wire (neutral) for a total of four conductors between the transformer
> and panel?
>
> 73/k5gw
>
>
> In a message dated 10/7/2005 12:57:13 P.M. Central Standard Time,
> baycock at direcway.com writes:
>
> Thats the way I see it. The only difference I have with Gary is in
> the
> connections between the panel and the transformer drop. There is an
> earth connection at each end, and only at each end, but my
> supplier has
> the added requirement of a metallic conductor between transformer
> neutral and panel ground, as well.
> Bill
>
> Red wrote:
>
> >I believe the single point ground is to hold all equipment
> grounds at a
> >common potential; so that there is no potential or voltage
> between any
> >two component grounds. Short and minimally inductive conductors
> from
> >equipment to that single point minimize that potential difference.
> >Equipment grounds and the single point ground must not be
> connected to
> >the system neutral, except at the service entrance and at the power
> >company equipment. There must be no path between system neutral and
> >ground anywhere else.
> >
> >73 de Red, WOØW
> >
> >Gary Schafer wrote:
> >
> >
> >
> >>With single point grounding for the antenna / power system the
> idea is
> >>to not have ground paths through any equipment to ground.
> >>
> >>73
> >>Gary K4FMX
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >>
> >
> >_______________________________________________
> >
> >See: http://www.mscomputer.com for "Self Supporting Towers",
> "Wireless Weather Stations", and lot's more. Call Toll Free,
> 1-800-333-9041 with any questions and ask for Sherman, W2FLA.
> >
> >_______________________________________________
> >TowerTalk mailing list
> >TowerTalk at contesting.com
> >http://lists.contesting.com/mailman/listinfo/towertalk
> >
> >
> >
> >
>
> --
> Bill Aycock W4BSG
> Woodville, Alabama
>
>
> _______________________________________________
>
> See: http://www.mscomputer.com for "Self Supporting Towers",
> "Wireless Weather Stations", and lot's more. Call Toll Free,
> 1-800-333-9041 with any questions and ask for Sherman, W2FLA.
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
>
>
--
Bill Aycock W4BSG
Woodville, Alabama
More information about the TowerTalk
mailing list