[TowerTalk] CQ article error(?)
    Jim Lux 
    jimlux at earthlink.net
       
    Fri Oct  7 18:30:17 EDT 2005
    
    
  
At 11:58 AM 10/7/2005, Gary Schafer wrote:
>You seem to be saying two different things here?
>
>The neutral wire IS to be grounded to earth along with the safety ground
>at the service panel. Both are tied together and connected to earth
>ground at the main service panel. The power company also grounds the
>neutral connection at the transformer to earth ground.
Not necessarily.. for the same reason as you have a single interconnect 
between neutral and ground.  You don't want neutral return currents flowing 
back to the transformer via the ground path.
Also, if the neutral opens between your house and the transformer (which 
does happen, particularly on an overhead service), you don't want the 
entire neutral return current flowing through ground.  You'd rather have 
the voltages on the two sides become unbalanced.  Radical voltage 
fluctations may destroy equipment, but at least it doesn't create a shock 
safety hazard.
I suspect, however, that there is some variation in local practice 
here.  It probably depends on things like how many loads are serviced from 
the transformer, how far the transformer is from the load, and so forth.
I seem to recall reading some fairly complex story about a swimming pool, a 
multiunit apartment  complex, and how the NEC required grounding strategy 
resulted in the pool being electrified.
>The neutral should never be grounded anywhere else.
>
>73
>Gary  K4FMX
    
    