It's important to understand what these devices do. These "whole house" 
units are simply BIG MOV's that attempt to conduct the surge to "short it 
out." In doing so, it must GO somewhere -- that is, current flows in some 
complete path. Remember that the neutral is bonded to ground at the service 
entrance, so there is no need for a protector between neutral and ground. A 
line to ground protector conducts the surge to ground, so when a surge hits, 
it will raise the potential of the safety ground (and neutral bus) by an 
amount equal to the IZ drop between the panel and whatever lightning thinks 
"earth" is. When you say "line-to-line," I assume you mean across the 240 
volt secondary of a 120-0-120 circuit.  

>but then, all the electronics plug 
>into "real" lightning protectors (usually TrippLite) before plugging
>into the wall

Your definition of "real" in this case is flawed. Nearly all AC line 
"lightning protectors" are nothing more than MOV's connected as noted above. 
When they take a hit, they shove the surge into the equipment ground wire at 
the outlet where they are plugged in, raising the potential at that outlet 
in the presence of a surge. If equipment plugged into a "protected outlet" 
is connected by low voltage wiring to equipment plugged into another un-
protected outlet, or even a DIFFERENT protected outlet, there can be large 
potential difference between outlets that can blow up equipment. Thus, 
typical power-strip MOV protectors are NOT "real" protectors. 

The "real thing" includes 1) a good whole house protector and/or 2) a 
SERIES-mode protector like those that SurgeX makes. I use SurgeX boxes, and 
plan to add a "whole house" unit at the service entrance. 

And, as has been pointed out on several occasions, it is critical that other 
lines (telco, antennas, etc.)that can bring lightning into the house be 
bonde and/or protected AT THE SAME POINT as the power line. Tom Rauch has 
pounded on this for quite a while, and he is right on. That's often a lot 
more difficult in some installations, but it's the right way to do it. 

Jim Brown  K9YC