[TowerTalk] OT: Generators and UPS's

Jim Lux jimlux at earthlink.net
Fri Aug 25 19:14:55 EDT 2006


At 01:54 PM 8/25/2006, you wrote:
>Tnx Jim for the info. The cheap thing would not be to go to a larger
>generator. This is a 16KW unit.

Ah.. yes.. that would be pretty pricey to go to the next step up...

If you don't have one, I'd beg or borrow an oscilloscope and look at the 
voltage waveforms.  You can capacitively couple the scope with a twist of 
wire around the hot lead if you don't have a suitable isolation or HV 
probe... you're not interested in precise voltage measurements, just 
whether the waveform is significantly not like a sinewave.