>however NEC bonds are NOT for RF and NOT for 
>lightning dissipation.
I'll take several issues with that. First, NEC bonding to earth 
electrodes IS specifically for lightning protection. That is the 
purpose of an earth connection. 
One function of NEC bonding between equipment enclosures is to 
provide a path that will blow a fuse or breaker if there is a 
fault that makes the chassis hot. Another function of bonding is 
to cause all parts of the electrical system in a home to rise 
together in the event of a strike, thus minimizing the DIFFERENCE 
between equipment that might be interconnected. It is often this 
difference that blows up equipment. Bonding everything together 
approximately limits that difference to the voltage induced on the 
bonding conductors. 
Second, lightning IS RF. IEEE studies show that most of the energy 
in lightning is in several octaves centered around 1 MHz (that is, 
from about 250 kHz to about 4 MHz). 
Third, there is no "RF" reason, other than lightning protection, 
for a connection to earth. A connection to earth does not improve 
the performance of antennas, it does not reduce noise, it does not 
reduce RFI. References saying that it does are WRONG, including 
statements in equipment manuals, ARRL publications, and even 
several questions in the current license exam pool! 
As to the bonding conductors themselves -- the primary problem 
with braid and other small stranded conductors is increased 
CORROSION if they are exposed to the elements. That's why they are 
not recommended for these applications. There's nothing wrong with 
using them if they are not exposed. I use braid for bonding inside 
my shack because it is beefy and more flexible. 
73,