[TowerTalk] Romex for Rotor cable?
Jim Brown
jim at audiosystemsgroup.com
Thu Mar 1 21:21:29 PST 2012
On 3/1/2012 5:10 PM, Steve Jones wrote:
> A while back on TowerTalk I saw a comment that a nice solution for long 8-conductor rotor cable runs is a pair of "12-3 with a ground" Romex cables,
Hi Steve,
I'm using two runs of 14-3 to run my Yaesu rotor. Total length is about
350 ft. Determined that it would work on the basis of Ohm's law and the
permitted IR drop for the model I'm using. It's laying on the ground.
I wouldn't do that if it was carrying 120VAC. :) This sort of cable
doesn't stand up to UV, but mine runs through a dense redwood forest, so
I'm not very worried. :)
The fundamental reason for the restrictions of various types of cable in
conduit is flamability and noxious fumes. It all came from "The Towering
Inferno" 25 or so years ago. For applications like this it doesn't matter.
73, Jim K9YC
More information about the TowerTalk
mailing list