[TowerTalk] Cadweld vs other welds or brazing

Jim Lux jimlux at earthlink.net
Sat May 3 09:44:58 EDT 2014


On 5/2/14, 6:04 PM, N3AE wrote:
> I've been following this thread with interest.
>
> What's the proper way to bond galvanized steel anchor rods to the
> rebar cage to get a good Ufer ground? The UST specs specifically
> state not to weld the rebar (because they call out ASTM A-615 rebar,
> not the weldable A-706).

tie it.

A variety of testing has shown that the metal conductors in a concrete 
encased grounding electrode do not have to be continuous.  There was one 
paper where they tested versions of Ufer grounds where the segments of 
rebar that were welded, segments that were tied, and segments that were 
just laid together.  They all worked acceptably.

I'm sure there are pathological cases: if you had a bunch of 6" long 
pieces of rebar randomly placed in a big block of concrete) that 
technically meet the 20 feet of conductor guideline; but, I would think 
that pretty much any "conventional" assembly technique would work.

It's mostly about providing a suitable large area contact with the 
surrounding soil, and after that, making the current density in the 
metal and at the metal to concrete interface low enough.

>
> My plan is to use bronze rebar ground clamps rated for direct burial
> for both the wire-tied rebar cage and the anchor rod connections,
> with #4 AWG solid copper wire between them and a bit of stainless
> shim stock between the clamps and the galvanized anchor rods (for the
> dissimilar metals problem - galvanized with copper-bronze clamps).
> All the above encapsulated in the concrete pour.
>
> Make sense? Are the SS shims overkill or even undesirable (compromise
> the tightness of the connection to the anchor rods)?
>
> Shawn - N3AE
>
> _______________________________________________
>
>
>
> _______________________________________________ TowerTalk mailing
> list TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
>



More information about the TowerTalk mailing list