[TowerTalk] [Bulk] Re: Cadwelding to Rohn 45G and 55G
Grant Saviers
grants2 at pacbell.net
Fri Feb 12 16:14:34 EST 2016
Ground (pipe/rod) clamps come in an bronze or brass alloy. For clamping
on galvanized steel, I think they are brass (Zn + Cu) but either may be ok?
I ran a 2 radials from each leg, that offers redundancy, lower
inductance, more capacitive ground coupling, and shortest paths. I
would not recommend a ground ring if you want to measure your ground rod
resistances. Any loops prevent that assuming the leads from it to the
rods are buried cadwelds. I've also a convert to using bare #2 stranded
3 rods per radial connection spaced 15' or more apart. One at 5' from
tower then 20 and 35' out. 9 rods or more if more radials. Best if
buried below the frost line as frozen water is a particulary poor
conductor.. The #2 also has enough surface area to act as a horizontal
grounding element. I started with #6 for the first set of rods, then
used some #2 and after some measurements became convinced #2 was worth it.
Grant KZ1W
On 2/12/2016 11:58 AM, Larry Loen wrote:
> That may be a nice alternative, but what advantage does it offer over
> simply connecting a regular ground clamp?
>
> It seems like a very nice idea, but I need to understand what I gain versus
> just clamping and having done with it. If I did the "classic" thing and
> cadwelded to the tower legs, I would not be depending on bolts.
>
> On the other hand, I'm already (arguably) depending on six sets of bolts
> "above" me to connect the top sections to the bottom tower section anyhow.
> You could argue: What's one more set of bolts?
>
> Anyone know what I would be trading-off here?
>
>
> WO7R
>
> On Fri, Feb 12, 2016 at 12:44 PM, <TexasRF at aol.com> wrote:
>
>> Larry, can you connect some tinned copper lugs to the lower set of three
>> (or six) leg bolts using the existing bolts? For added security, you could
>> add six locking nuts. The ground wires would then connect to the lugs of
>> course.
>>
>> 73,
>> Gerald K5GW
>>
>>
>>
>> In a message dated 2/12/2016 1:39:10 P.M. Central Standard Time,
>> lwloen at gmail.com writes:
>>
>> I am in the process of putting in two new towers on my property (yes, I am
>> blessed).
>>
>> I'm a little nervous about Cadwelding to the legs. I suppose you'll all
>> tell me it has been done dozens of times, but I have visions of blowing a
>> hole through one of the legs near the bottom of my tower.
>>
>> The alternative, I suppose, is to get a set of quality ground clamps, clamp
>> it maybe three times (I assume this would help the impedance a bit) and the
>> inspect it over time.
>>
>> I also plan to have an extensive "ground ring" around the tower. On my
>> current crankup, I cadwelded to all three "legs" except it was easy to
>> Cadweld to a nice thick base and not to the tower, proper. Effectively
>> required, in fact. So, I Cadwelded to stuff that wasn't a big deal,
>> structurally. Here it would be.
>>
>> 1. Do I Cadweld anyway? How to be sure the tower leg isn't weakened?
>>
>> 2. Do I do it to a single leg or all three? I could "feed" my ground ring
>> from a single leg, I suppose.
>>
>> This is all in excess of what Rohn shows, which is a single, clamped line
>> from the tower, but I've always taken it for granted the smart thing to do
>> is have a more extensive network. I plan on three rods, connected as a
>> ring, and then copper "lines" out from each of them to another rod, a total
>> of six in all. That's all easy and been done (by me) before. Question is,
>> what's the best way to connect to the tower itself? I have the "buried
>> tower section" type of base. We will be pouring concrete late next week.
>> So, I have about a month to plan and execute my ground system.
>>
>>
>> Larry WO7R
>> _______________________________________________
>>
>>
>>
>> _______________________________________________
>> TowerTalk mailing list
>> TowerTalk at contesting.com
>> http://lists.contesting.com/mailman/listinfo/towertalk
>>
>>
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
>
More information about the TowerTalk
mailing list