[TowerTalk] Fwd: Grounding connection to tower legs (Kevin Stover, AC0H)
Grant Saviers
grants2 at pacbell.net
Tue Oct 17 10:29:22 EDT 2017
One more alternative is to use a DX Eng saddle clamp and extend the
saddle backing plate far enough to use two hole lugs. I made the
backing plate out of 1/4 x 1-1/2" 6061 and wide enough for two lugs each
side. One clamp on each leg with 2 or 3 #6 or #2 wires to pairs of
buried 8' rods Cadwelded. I put some contact goop in the saddle area
where it contacts the tower. 2" saddles for Rohn 65 are a very close
fit. A few dollars cheaper than the Rohn similar idea, and uses two
hole lugs. Aluminum against zinc is pretty benign electrochemically.
Grant KZ1W
On 10/16/2017 11:58 AM, Jim Brown wrote:
> On 10/15/2017 7:35 PM, Ward Silver wrote:
>> Use a proper clamp designed to connect copper wire to galvanized
>> tower legs. For Rohn 25, the clamp is part number R/CPC-1.25
>
> Here are two sources with what seem to be the best prices. If you poke
> deeper, you learn that the two links are simply different DBAs for the
> same business. :) $30 each.
>
> https://www.cableandwireshop.com/rohn-tower-grounding.html
>
> https://www.3starinc.com/rohn_r-cpc11_25_tower_base_ground_clamp.html
>
> I just ordered clamps to replace the stainless steel hose clamps that
> I'm currently using. The website let me place an order without adding
> yet another password. :)
>
> 73, Jim K9YC
>