[TowerTalk] How critical is the 120 degree ...

K9MA k9ma at sdellington.us
Tue Jul 27 23:53:29 EDT 2021


Both cases are fairly simple vector analyses. Deviating from the 120 
degree spacing will result in increased tension on some of the guys, as 
well as vertical load on the tower.. You can calculate that, and 
increase the size of the guy wires and anchors, if necessary. Likewise 
the distance to the guy points: the closer they are to the tower, the 
greater the tension on the guys and the greater the vertical load on the 
tower. If you can't do the calculations yourself, or if required by 
local codes, consult a professional.

By the way, the convenient thing about the 120 degree spacing is, 
assuming all the guys are anchored at the same distance from the tower 
and same elevation, the worst case tension in a single guy is just the 
same as the tension in one guy with the wind blowing directly from the 
anchor point to the tower, i. e. , directly in line with one guy. If the 
wind happens to be blowing exactly between two guys, each will see that 
same tension. It's more complicated if the spacing is different. 
Changing just the spacing between two guys to 130 degrees increases the 
maximum guy tension by about 20 percent. (cos60/cos65)

Keep in mind that this all comes from Engineering Mechanics 101 nearly 
50 years ago. We electrical types all hated that course, but it's been 
one of the most useful to me.

73,
Scott K9MA

On 7/27/2021 1:00 PM, David Gilbert wrote:
>
> The first question seem like a rather simple vector analysis task to 
> me.  Generate a simple model for the manufacturer's recommendations 
> for included angles, distance from tower, and guy wire tension ... and 
> then calculate the lateral force on the tower due to each guy wire.  
> Do the same analysis for the configuration under consideration (with 
> the addition of translating the resulting forces to the desired 
> directions of 120 degrees apart) and compare the resulting lateral 
> forces.  Decide how much deviation from the spec you're willing to 
> live with (5%? ... 10% ... whatever) and see if it satisfies.  Keep in 
> mind that any change in guy wire tension to compensate for deviations 
> from the tower manufacturer's configuration needs to stay within the 
> guy wire ratings.
>
> Seems like a better approach to me than relying on the opinion of 
> anyone, although my opinion says that when you do the calculation you 
> would find that the difference between 1 degree deviation and 2 
> degrees deviation is round off error.
>
> 73,
> Dave   AB7E
>
>
>
> On 7/27/2021 12:47 AM, Jari Jussila wrote:
>> Hi ...
>>
>> I'm sure these topics have been discussed earlier, but could not find 
>> any thread ..... Sri ...
>>
>> We are at our club erecting two towers. A rotating steel tower being 
>> 31 m high and a aluminium telescope mast 18+18 m = 32 meters.
>>
>>
>> A) How critical is the rule that guy wires should be "exactly" 120 
>> degrees apart?
>> A professional guide says, that the anchor point can be 50 mm from 
>> that 120 degree (119,9-120,1 degree) but some say, that a maximum of 
>> two degrees is OK. That meaning 118-122 degree.
>>
>> What's the tower community advise?
>>
>>
>> B) The steel tower height is 31 m - it's a rotating tower - but the 
>> upper bearing is at 23 m ( leaving 8 meters for the antennas) and the 
>> lower bearing at 11 meters.
>>
>> Whats the advise of anchor point distance? Some say, that the 60 % 
>> (distance for  the tower) should be calculating from the total height 
>> (31 x 0,6 = 18,6 meters).
>> Some say, it should be calculating from  the upper bearing (23 m x 
>> 0,6 = 12.8 m)
>>
>> Whats your opinion?
>>
>> Jari, OH2BU
>> For OH3AC Club Station
>>
>
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk


-- 
Scott  K9MA

k9ma at sdellington.us



More information about the TowerTalk mailing list