Ed:

This is no different from the noise change that occurs when the sun goes down, 
so all it really does is demonstrate that the noise is coming from some part of 
the system.
That's correct. The reason my neighbor and I had to resort to covering 
the panels was to show that the system was still generating RFI after 
the chokes were applied to the optimizers. Solar Edge insisted that the 
chokes had resolved this issue and we proved otherwise.
The only way to completely shut down the system during the day is to 
cover the panels.
By the description here, the first major noise source, the optimizers, seems to 
have been corrected.
That has yet to be determined Ed. Tom Simpson (SE engineer) believes the 
RFI could be caused by the solar panels themselves which he said has 
happened in the past.
This idea of guessing or theorizing what component is causing the noise 
could have been resolved a long time ago if Solar Edge would agree to 
disconnect the ALL panels from the system and probe each component to 
see which one is causing the RFI.
I've been at the site each time SE has worked on the system and they've 
NEVER removed all the panels at once. This would, at the very least show 
that there's a problem with the panels and or optimizers.
I'm hoping that yourself or perhaps Paul can convince Tom Simpson to do 
so when he visits the site. If not, we're just going around in circles.
Tony -K2MO







On 9/28/2020 3:13 PM, Hare, Ed W1RFI wrote:
<We were able to isolate the noise from the solar panels and associated 
electronics by covering the      panels and seeing it disappear.>

This is no different from the noise change that occurs when the sun goes down, 
so all it really does is demonstrate that the noise is coming from some part of 
the system.

By the description here, the first major noise source, the optimizers, seems to 
have been corrected.  The inverter noise appears to still be present. This is 
an area that Paul and Solar Edge are investigating and working on, so let's 
give that a bit of time to develop. Paul owns the system, and he is qualified 
to work on it, so when they come up with possible ideas, he is able to do the 
work without having to coordinate with a neighbor.

-----Original Message-----
From: RFI <rfi-bounces+w1rfi=arrl.org@contesting.com> On Behalf Of Tony
Sent: Monday, September 28, 2020 2:55 PM
To: Cianciolo, Paul, W1VLF <pcianciolo@arrl.org>; Rfi List <rfi@contesting.com>
Subject: Re: [RFI] Question Regarding Variations In Solar Panel RFI?

Paul:

The RFI on the home AC lines is identical to the RFI generated by the Solar 
Edge system. I can't tell you if it's induced or directly injected onto the A/C 
lines but it's there.

More importantly, the RFI on the AC lines disappears when the system shuts down 
either by covering the solar panels with tarps or when the system automatically 
shuts down at night.

Here's what we know for certain after months of testing and observation:

1. The inverter and optimizers produce a distinct noise of their own.
2. The noise disappeared completely when we covered the solar panels with tarps.
3. The noise reappears when we removed the tarps.
4. The noise appears at sunrise and disappears at sundown.
5. We were able to isolate the noise from the inverter by shutting it off and 
seeing the spikes disappear.
6. We were able to isolate the noise from the solar panels and associated electronics by covering 
the      panels and seeing it disappear.

Solar Edge recently replaced the inverter on the 18th of August and I recorded 
the event from start to finish. What it showed was that the inverter spikes 
disappeared while the inverter was removed from the system and then re-appeared 
once the new inverter was installed and activated.

I'll post the link to the time lapse video I recorded ASAP.

Good to hear from you Paul. Let me know if you need further information.

Tony -K2MO






On 9/28/2020 10:23 AM, Cianciolo, Paul, W1VLF wrote:
Tony,

Regarding your statement below:

"We found high levels of RFI on the A/C lines throughout my neighbor's home and 
that's likely the case with all Solar Edge installations .............since there are no 
chokes between the mains and inverter."

It is the last part that I take issue with.  See the attached photo.
This is the EMI filter on the SE inverter on my house.  Also see the
attached PDF, look under page 3 COMPLIANCES  you will find part 15B
They could not legally connect these to a residential  AC line if it
were not part 15b compliant. In addition I have a Corcom 25fc10
installed at my home.  See the data sheet and response curves here.
http://www.farnell.com/datasheets/1430489.pdf
The filter makes a barely detectable change in the any received RFI I have from 
the SE system.

What needs to happen here is to determine,  the source of the RFI first, not 
the radiating elements.    In the past you have mentioned that even with the 
inverter off, not producing power, you still had the interference. In fact you 
had covered the panels and the RFI went away.

With that in mind here are a couple of sources, or generators, and not he 
radiating element that I cab confirm in my testing.

1) The inverter itself. The original inverters SE used had an internal
switching frequency of roughly 18 KHz and thus harmonics were found
every 18 KHz
2) The HD wave inverters operate at roughly 50 KHz and thus you can see 
harmonic energy at 50 KHZ intervals  Other manufacturers that I have worked 
with use 39 KHZ .
It is difficult to switch, in my case 6.5 Kilowatts of power in a box 12" x 12" by 
8"
3) The original optimizers as we all know had a serious 200 KHz problem.  In 
the next version, as I have in my installation that problem has been rectified.
4) This leaves the fact that the current optimizers, the SP350? I believe?  may 
still generate  some noise in the non-power generating state. I am pretty sure 
you sent me a video or photo comparison that Randy, sorry I forget his call at 
the moment,  but he did bench test on a non-power generating optimizer.

In that video, you showed the spectral waveforms looking similar I believe?

I don't think the inverter is the cause of your issues at that this point. The 
exact radiation mechanism of the RFI from your neighbors SE system is still 
unknown.
I also do not see the noise issue you have, as you previously described at my 
house. The again I only have a 275' open wire fed dipole that I tune on all HF 
bands 200 feet away from house.  I don not have a multielement beam design for 
20 meters.

To me it would make the most sense to concentrate on the specific device 
generating your noise based on the RF signature.


73,

Paul Cianciolo, W1VLF
ARRL EMC Engineer

ARRL - The national association for Amateur RadioT
225 Main Street, Newington, CT 06111-1400 USA
Telephone: (860) 594-0392
FAX: (860) 594-0259
Email: w1vlf@arrl.org
World Wide Web: www.arrl.org








-----Original Message-----
From: RFI <rfi-bounces+pcianciolo=arrl.org@contesting.com> On Behalf
Of Tony
Sent: Friday, September 25, 2020 6:23 PM
To: Rfi List <rfi@contesting.com>
Subject: [RFI] Question Regarding Variations In Solar Panel RFI?

All:

The reports I've read suggest that the strength of interference caused by solar 
panel systems can vary from one installation to the next EVEN when the distance 
to the source is similar. That variation could be attributed to radiating 
conductors tied to the system such as the house wiring.

We found high levels of RFI on the A/C lines throughout my neighbors home and 
that's likely the case with all Solar Edge installations since there are no 
chokes between the mains and inverter.

Given those facts, would a large home with long runs of un-shielded Romex 
produce higher levels of interference compared to a smaller home with shorter 
runs? Or does the resonance of the wiring play more of a role than length and 
number of runs?

It's an oversimplification, but it seems logical to consider what's connected 
to system and not just the system itself.

Tony -K2MO

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi
<Prev in Thread] Current Thread [Next in Thread>