On Sun, 21 Mar 2010 15:42:54 -0400, Paul Christensen wrote:
>BTW, the material that Jim Brown (K9YC) referenced from SurgeX is excellent.
Thanks, Paul.
>In thinking the secondary suppressor problem through, I thought that only a 
>"single-mode" L-N bypass to neutral (rather than ground) would prevent a 
>ground potential rise between branch circuits. 
That's right. It's the MOV to ground that causes problems.  
>Those devices exist, but apparently, they still do not provide as high 
>degree of protection than the technology used by SurgeX.
That's the way I see it.  The SurgeX stuff is expensive. When I'm specifying 
sound systems, I put SurgeX boxes on the gear that is relatively expensive 
and more likely to have issues with power line spikes. A 20A SurgeX unit that 
costs about $500 can protect $100K worth of DSP gear, mixing equipment, EFX 
boxes, etc. In terms of cost effectiveness and risk, that's a pretty good 
ratio.l But I am less likely to specify them to protect power amps, where I 
typically must put only 2-4 power amps on one SurgeX unit (because the 
current draw of power amps often requires a circuit for every 2-4 power amps) 
with a cost of only a few $K.  
73,
Jim K9YC