On 1/27/2014 10:27 PM, Jim Thomson wrote:
Date: Sun, 26 Jan 2014 17:34:28 -0800
From: Jim Brown <jim@audiosystemsgroup.com>
To: amps@contesting.com
Subject: Re: [Amps] MOVs
On 1/26/2014 2:57 PM, Michael Tope wrote:
This is probably a dumb question, but why not put the MOV between hot
and neutral? If the spike is differential mode, that would kill it
without spiking current into the safety ground.
Between hot and neutral on a 120V branch circuit is fine. Also OK
between Line and Line on 240V.
Be careful though, many an old house has had the neutral grounded in the
outlet instead of back at the panel.
73
Roger (K8RI)
73, Jim K9YC
### I mentioned in a previous post about wiring movs from line to neutral.
Whether you install movs from line to line or line to neutral.... make damn
sure they are FUSED. MOVs consist of a lot of grains in series..and every
time a transient, surge, spike comes down the line, a few grains here and there
will fail shorted. Eventually the Mov V rating will keep dropping. Once its
low
enough, it will conduct with just the normal 120 vac. Or 240 if line to line.
Boom, there goes the mov, blown to pieces. I wouldn’t rely on the breaker
in your main panel, or any fuses in the amp, end device etc, to stop the
destruction.
You require the correct type of fuse and size to fuse a mov.
## Newer style movs have a 3rd wire..with the center wire slightly offset to
one side...so they
cant be installed backwards in a pc board. These types are internally
fused..and are wired with
a led etc. If you see the led not lit... you know the internal mov fuse has
blown open...and you
have no protection. Several hundred house fires were caused in one year
alone...all from movs burning up.
## MOVs are not the only way to provide some protection from transients and
surges and spikes etc.
Saturable reactor style transformers, like SOLA constant voltage transformers
will also offer a degree of protection.
Yet another method is to use PI filters. They use large torroids with heavy
gauge wire plus UL rated caps plus movs.
Windings used in both the neutral and hot sides of a 120 vac circuit. They can
be used with several pi sections in series.
The commercial 4 outlet box I use offers 50 db of suppression in the 1st 2
outlets....and 70 db in the 2nd pair of outlets.
One PI filter feeds the 1st set of 120 vac outlets. A 2nd PI filter is between
the 2 sets of outlets. The 2nd pair of 120 vac
outlets gets the benefit of both PI filters.
Jim VE7RF
_______________________________________________
Amps mailing list
Amps@contesting.com
http://lists.contesting.com/mailman/listinfo/amps
---
This email is free from viruses and malware because avast! Antivirus protection
is active.
http://www.avast.com
_______________________________________________
Amps mailing list
Amps@contesting.com
http://lists.contesting.com/mailman/listinfo/amps
|