On 5/18/14, 7:39 AM, Roger (K8RI) on TT wrote:

 From the dictionary:  There is no need to go any farther.  Forget your
calculations, this is the definition.

Electrical resistivity quantifies how strongly a given material opposes
the flow of electric current. A low resistivity indicates a material
that readily allows the movement of electric charge. Resistivity is
commonly represented by the Greek letter ρ.


The SI unit of electrical
resistivity is the ohm⋅metre although other units like ohm⋅centimetre
are also in use.

Seems like what I was saying, no?

 *As an example, if a 1 m × 1 m × 1 m solid cube of
material has sheet contacts on two opposite faces, and the resistance
between these contacts is 1 Ω, then the resistivity of the material is 1
Ω⋅m.* (that is misleading as the formula actually  gives ohms per cubic
meter, not ohms per meter.

Actually not.. if the resistance between the two faces is R ohms, then the resistivity (rho) is rho=R * Area/length which has units of Ohms * meters


Please note Resistivity is in ohms per cubic Centimeter or ohms per
cubic meter not ohms per meter, or centimeter as is often stated which
is incorrect.

Yes, I agree, there's no "ohms/meter"


The resistance has to be proportional to length (distance between electrodes), because if you double the length, the resistance doubles.

Likewise, the resistance is inversely proportional to the cross sectional area (put two identical bars in parallel, and the resistance is half the resistance of a single bar).

Therefore, so if you have a property called "resistivity" which turns into "resistance" by factoring in the geometry, it has to be

R = Length/Area * rho.

Since Length/Area has units of 1/length (1/meters), and R is in ohms, then rho has to be ohms * meters, so that when you do ohms * meters * (1/meters) it comes out as ohms.


I note that a lot of software and tables mis-identify conductivity (not conductance) and resistivity. More than one table shows resistivity as ohms/meter, which is, of course, in correct. Ditto for conductivty, you'll see Siemen-meter or mho-cm, when it should be Siemen/meter or mho/cm

And that doesn't even get into when you look at older texts before units were systematized. Take a look at NBS pubs from the early 20th century or handbooks of the era and you see a lot of weird units (for instance, inductance specified in terms of length). For any consistent system of units you get 3 that are nice easy numbers, and one oddball one with weird constants (usually involving 4*pi or its inverse).

When calculating you must use ohms cc^3 or M^3 for the units to properly
cancel.

I don't think so.. can you show an example using cubic units?

I can give one using ohm-meters as resistivity.

Calculate the current through a concrete bar that is 10 ohm-meter resistivity. The bar is 1 meter long and 10x10 cm in cross section. A voltage of 1000 Volts is applied to the long axis of the bar.

R = 10 ohm-meter * 1 meter / (0.1 * 0.1 meter^2) = 10/0.01 = 1000 ohms.
I = V/R, so current is 1 Amp.
The current density is 100 Amps/square meter = 1 Amp/ 0.01 square meters

If one makes the bar 20x20 cm, what is the current?
R = 10*1 /0.04 = 250 ohms
The current density is 4 amps / 0.04 square meters or the same 100 Amps/square meter, which makes sense, because the voltage between the ends is the same (1000V) and the current is flowing "along" the bar, not crossways


A more complex question.. Given that the soil has a conductivity (sigma) of 5 mS/m, what is the current flow through a 2 meter trough which is 30x30cm with 10,000 volts along the length it?

The conductance G is sigma * Area/Length = 0.005 * 0.09/2 Siemens = 0.000225 Siemens (or mhos).

I = G * V

So, I = 2.25E-4 * 1E4 = 2.25 Amps

so the current is 4 Amps



Too many texts use the simplified versions which are misleading.



73

Roger (K8RI)

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk
<Prev in Thread] Current Thread [Next in Thread>