[Amps] Dedicated 220AC Wiring for Amps..

R.Measures r at somis.org
Thu Oct 13 15:15:43 EDT 2005


On Oct 13, 2005, at 10:41 AM, monty taylor wrote:

> This brings up a question I have.  I am using my pre-wired dryer 
> outlet,
> 30 amp breaker, #10 wire; red, black and white.  It has only three
> conductors and no ground wire, just; hot, hot, and neutral.  The house
> is 10 years old and code approved.  For the amp, an AL1500, I wired per
> the instruction manual for 220 Volts, hot, hot and neutral to the
> ground/chassis connection.  Now, I want to RF/AC ground the chassis to 
> a
> different 8ft copper clad ground rod.  I read that you should never
> connect neutral and ground together at any place other than the entry
> panel as a difference in voltage potential could exist.

Could is not very likely since if there an anomaly and there is enough 
unbalance current to cause much v-drop in the neutral wire, the 240v 
breakers trip and the voltage goes to zero.   Whoever wrote the new NEC 
needs to take a course in circuit analysis.

> The #10 run to
> the dryer outlet is about 30 feet.  My question: Should I ground the 
> amp
> to the new rod outside my shack or not?  I have been using the shack
> with out any ground rods so far; only at the far end of all my coax 
> runs
> through lightning surge protectors.
>
> A little wordy, but I hope I get some answers.
>
> Best regards,
> Monty/WB5GLB since 1969
>
>
> _______________________________________________
> Amps mailing list
> Amps at contesting.com
> http://lists.contesting.com/mailman/listinfo/amps
>
>

Richard L. Measures, AG6K, 805.386.3734.  www.somis.org



More information about the Amps mailing list