One very good way to do it is what K4XU did in the Ten Tec Titan 425 
(circa 1978-9), whose power xfmr has two windings that are strapped in 
series for 240V and in parallel for 120V. When strapped for 240V, 120V 
is obtained from one of the primaries.

Last I looked, it is a code violation for the Green Wire to carry load 
current. Older appliances did that, but while ancient installs are 
grandfathered, it has been prohibited for new installations for decades.

73, Jim K9YC

On 5/4/2021 1:54 PM, w5cul at sbcglobal.net wrote:
> I think what was being said there is that if an Amp has 110Vac Fans, then
> there should be an independent Neutral associated with the Amp as well, to
> include L1, L2 and Ground.  I think what was being implied is that the
> Neutral to the Amp would NOT be bonded to the Chassis Ground, yet serve
> solely as a return for the 110Vac Fans.