[TowerTalk] Conduit for cables to the tower?
Keith Dutson
kdutson at sbcglobal.net
Fri Sep 15 16:56:06 EDT 2006
Thanks for posting about the ground. I was planning to connect all towers
together using 2awg solid tinned copper wire. I have one roll of 500 feet
to use for the ground rod connections for each tower but would need two more
rolls to tie them together. That roll cost $500 a year ago. I was not
looking forward to pricing two more.
73, Keith NM5G
-----Original Message-----
From: towertalk-bounces at contesting.com
[mailto:towertalk-bounces at contesting.com] On Behalf Of Dick Green WC1M
Sent: Thursday, September 14, 2006 10:53 PM
To: 'Nick Pair'; towertalk at contesting.com
Subject: Re: [TowerTalk] Conduit for cables to the tower?
> I don't see the need for GRC conduit but do see the need for a
> grounding wire to tye the tower system to the SPG shack ground and
> service entrance ground.
I read somewhere, I think in Polyphaser's documentation, that the need to
connect the tower ground with the shack ground and service entrance ground
depends on the distance between them. As I recall, if the ground systems are
more than 75 feet apart, they don't "see" each other across the wire
connection. As I recall, the wire impedance prevents the surge from
propagating more than 75 feet. Another way to think about it is that the
wire impedance is too high for the voltages above ground at both ends to
equalize.
I'd be interested in knowledgeable comments on this issue. Before I found
that Polyphaser reference, I threw 265' of stranded 1/0 wire in the trench
between my crankup tower and shack in order to connect the ground systems.
I'm in the process of putting in another tower with its own ground system
that will be 220 feet from the shack. In the nine years since I did the
first tower, the price of 1/0 stranded wire has gone up to $2.10 per foot.
If the Polyphaser literature is correct, I'd be wasting $462 if I threw a
run of 1/0 wire in the trench to connect the tower and shack ground systems.
Another consideration is that there will be two runs of 1 5/8" heliax in the
trench. I have to believe those two 2" copper tubes will have a much lower
impedance than 1/2" of 1/0 stranded copper wire. I would think a surge would
travel up those "pipes" in preference to the 1/0 wire.
Knowledgable opinions?
73, Dick WC1M
_______________________________________________
_______________________________________________
TowerTalk mailing list
TowerTalk at contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk
More information about the TowerTalk
mailing list