Subject: Re: [Amps] TL922 Power Plugs
From: Ian Hill - K8MM <ihk8mm@charter.net>
Date: Tue, 03 Nov 2009 11:49:26 -0500
List-post: <amps@contesting.com">mailto:amps@contesting.com>
You beat me to it....lol

Ian - K8MM

maflynn@att.net wrote:
> Not allowed by code:  NFPA 70: 408.20 Grounding of Panelboards. Panelboard 
> cabinets and panelboard frames, if of metal, shall be in physical contact 
> with each other and shall be grounded. Where the panelboard is used with 
> nonmetallic raceway or cable or where separate grounding conductors are 
> provided, a terminal bar for the grounding conductors shall be secured inside 
> the cabinet. The terminal bar shall be bonded to the cabinet and panelboard 
> frame, if of metal; otherwise it shall be connected to the grounding 
> conductor that is run with the conductors feeding the panelboard.
>
>
> Grounding conductors shall not be connected to a terminal bar provided for 
> grounded conductors (may be a neutral) unless the bar is identified for the 
> purpose and is located where interconnection between equipment grounding 
> conductors and grounded circuit conductors is permitted or required by 
> Article 250.
>
>
> -------------- Original message from "Mark Robinson" 
> <markrob@mindspring.com>: -------------- 
>
>
>   
>> My Neutral and Ground is connected at the main panel but also at the barn 
>> 300 feet away. I am running a 3 wire 100 amp 240v power 4 00 aluminum line 
>> to the barn from a 100 amp 240v breaker located in my main distribution box. 
>> I didn't like the idea of a gnd neutral tie that far away from the barn, so 
>> I tied them together at the barn with a second ground rod located at the 
>> barn. Is that such a bad idea? 
>>
>> Mark 
>>
>>
>> ----- Original Message ----- 
>> From: "Ian Hill - K8MM" 
>> Cc: 
>> Sent: Tuesday, 03 November, 2009 10:24 AM 
>> Subject: Re: [Amps] TL922 Power Plugs 
>>
>>
>>     
>>> There isn't anything ILLEGAL about connecting the neutral and ground 
>>> anywhere else beside the main panel. You're violating the NEC but not 
>>> committing a criminal offense. ;-) 
>>>
>>> K8MM 
>>>
>>>
>>> Jim Brown wrote: 
>>>       
>>>> On Thu, 29 Oct 2009 18:17:21 -0400, Ian Hill - K8MM wrote: 
>>>>
>>>>
>>>>         
>>>>> Houses are typically feed off of a center tapped secondary. 240V 
>>>>> measured between phase conductors and 120V between either phase 
>>>>> conductor and the center tap. There isn't any sort of dangerous short 
>>>>> by having the neutral ( i.e. center tap) and the ground bonded together 
>>>>> in the primary distribution panel in a house....its supposed to be 
>>>>> connected that way. 
>>>>>
>>>>>           
>>>> Exactly right. One other VERY important point -- it is both ILLEGAL and 
>>>> UNSAFE to connect neutral to ground at any other point. The proper 
>>>> connection of a 240V load is to the two ends of the transformer only, 
>>>> and with the ground wire connected for safety. 
>>>>
>>>> There is some equipment that needs both 240V and 120V to operate. That 
>>>> equipment gets its 240V from the two ends of the transformer, and MUST 
>>>> get 120V between one side of the transformer and NEUTRAL, NOT GROUND. 
>>>>
>>>> 73, 
>>>>
>>>> Jim Brown K9YC 
>>>>
>>>>
>>>>
>>>> _______________________________________________ 
>>>> Amps mailing list 
>>>> Amps@contesting.com 
>>>> http://lists.contesting.com/mailman/listinfo/amps 
>>>>
>>>>
>>>>         
>>> _______________________________________________ 
>>> Amps mailing list 
>>> Amps@contesting.com 
>>> http://lists.contesting.com/mailman/listinfo/amps 
>>>       
>> _______________________________________________ 
>> Amps mailing list 
>> Amps@contesting.com 
>> http://lists.contesting.com/mailman/listinfo/amps 
>>     
> _______________________________________________
> Amps mailing list
> Amps@contesting.com
> http://lists.contesting.com/mailman/listinfo/amps
>
>   

_______________________________________________
Amps mailing list
Amps@contesting.com
http://lists.contesting.com/mailman/listinfo/amps

<Prev in Thread] Current Thread [Next in Thread>