> If I am following what you are saying that is not correct. Under the old
> rules with a 3 wire feeder to a detached building the neutral was to be
> connected to the neutral and ground buss in the panel in the remote
> building. A local ground rod was also to be installed and connected to the
> neutral/ground buss at the detached building.

Gary,

Pre-2008 NEC, that's allowable as long as there is no other metallic path 
between structures.  It still appears to be an allowable exception on some 
existing wiring with conditions.  Myself, I would convert the path between 
structures to 4-wire if reasonably possible.

Paul, W9AC 