On 8/22/2013 2:58 PM, Charlie Gallo wrote:
Well, there was some arcing at the ground block in the past, so I lifted the 
coax to slip on the ferrites, and the voltage is still there, but the current 
is low enough the ground takes care of it - ground clamp was a bit loose to, 
cleaned and tightened that

In normal (non-fault) operation, grounds should NEVER carry AC currents greater than a few mA. Likewise, the voltage between grounded objects or conductors should NEVER be greater than a volt or so. If there is voltage or current greater than these values, SOMETHING IS SERIOUSLY WRONG. The legal limit for leakage current (current on the green wire) in a branch circuit is 6 mA.

Always consider at least these four possibilities, and test to make sure that none exist.

1) An AC outlet may be wired with conductors reversed.

2) The equipment connected to the remote cable (in this case, the CATV cable) has a serious AC fault condition (perhaps that mis-wiring problem, or a very major grounding or bonding error).

3) Your equipment may be defective or have a fault condition.

4) There may be a problem (fault or mis-wire) in the mains power system supplying you or that remote equipment.

One of the most important pieces of equipment we should all own is a clamp-on AC ammeter that can be set to read small AC currents. This generally requires a low current scale where the top of the scale is no more than about 5A, and a 1A scale is better.

To use a clamp-on ammeter, we must be able to clamp it around a single conductor. Inside the breaker panel, that's fairly easy, but to measure current anywhere else (like at an outlet), we need a simple breakout cable. I have made breakout cables by cutting away a foot or so the outer jacket of a short AC extension cable, exposing the individual conductors. I plug the cable into the outlet and the equipment into the other end of the cable.

73, Jim K9YC