On 5/20/2014 10:02 PM, Grant Saviers wrote: So why are x uH's of green wire inductance ok in the three wire case and not for a single green wire (engineering pls, not UL regs)? First, if all three conductors go through the choke, a fault on the circuit will blow a breaker faster. Second, at RF, the capacitance between conductors tends to put the conductors in parallel. 73, Jim K9YC _______________________________________________ _______________________________________________ TowerTalk mailing list TowerTalk@contesting.com http://lists.contesting.com/mailman/listinfo/towertalk |