Towertalk
[Top] [All Lists]

Re: [TowerTalk] Ground rod

To: [email protected]
Subject: Re: [TowerTalk] Ground rod
From: David Gilbert <[email protected]>
Date: Tue, 16 Jul 2013 20:45:49 -0700
List-post: <[email protected]">mailto:[email protected]>

Please explain why. I understand why the rebar should not penetrate the soil/concrete interface, but I don't understand at all why a copper wire shouldn't.

73,
Dave   AB7E




On 7/16/2013 7:53 PM, Jim Lux wrote:


What is *really really* important is that NOTHING should penetrate the concrete/soil interface. No rebar sticking out of the side of the concrete below grade. No copper wires sticking out to bond to ground rods. No rods sticking out the bottom of the concrete. Only concrete should be touching soil.



_______________________________________________



_______________________________________________
TowerTalk mailing list
[email protected]
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>