1. [Amps] 220V service for amplifier (score: 1)
Author: Jason Buchanan <jsb@digistar.com>
Date: Mon, 01 Dec 2003 22:19:54 -0500
I did some searching through the list but haven't managed to hit the nail right on the head yet... For wiring a Ten-Tec Centurion amp to 220V, are there any recommended plugs and outlets to use? I am
/archives//html/Amps/2003-12/msg00019.html (7,248 bytes)

2. Re: [Amps] 220V service for amplifier (score: 1)
Author: Brian Moran <brianmo@yahoo.com>
Date: Tue, 2 Dec 2003 10:52:02 -0800 (PST)
Suggest trying the 6-20p plug/receptacle. Some of the dryer plugs/receptacles aren't rated for many plugs/unplugs. The 6-20p may also be less expensive, and you can find appliance "extension cords" f
/archives//html/Amps/2003-12/msg00022.html (9,181 bytes)

3. Re: [Amps] 220V service for amplifier (score: 1)
Author: Joe Isabella <n3ji@yahoo.com>
Date: Tue, 2 Dec 2003 09:02:01 -0800 (PST)
Jason, The "old" standard was only three wires for dryers (two Hots and a Neutral), but I'm pretty sure that new homes have 4 wire dryer outlets now. Consider the Neutral to be ground, since they are
/archives//html/Amps/2003-12/msg00023.html (9,052 bytes)

4. Re: [Amps] 220V service for amplifier (score: 1)
Author: Ed Briggs <edbriggs@optonline.net>
Date: Tue, 02 Dec 2003 15:40:32 -0500
Use a NEMA 6-20R and corresponding plug. For 20 amps, you need #12 conductors or larger. I use 3 #10 conductors with a 20 amp circuit breaker on my Centurion. The three conductors to the Centurion an
/archives//html/Amps/2003-12/msg00024.html (9,339 bytes)

5. Re: [Amps] 220V service for amplifier (score: 1)
Author: ka1xo@juno.com
Date: Wed, 3 Dec 2003 07:24:33 GMT
Dear Jason, On your amplifier there will more than likely be an attachment to the metal box where a grounding conductor can terminate. The metal frame of your amplifier should have an independent gro
/archives//html/Amps/2003-12/msg00030.html (8,672 bytes)

6. Re: [Amps] 220V service for amplifier (score: 1)
Author: "Bill Coleman" <n2bc@stny.rr.com>
Date: Wed, 3 Dec 2003 08:23:37 -0500
NEVER 'consider' or tie neutral to ground. They are NOT the same.... Neutral carries current by design, the ground should never carry current unless there is a fault. Neutral), but I'm pretty sure gr
/archives//html/Amps/2003-12/msg00032.html (10,188 bytes)

7. Re: [Amps] 220V service for amplifier (score: 1)
Author: jsb@digistar.com
Date: Wed, 3 Dec 2003 09:17:51 -0500 (EST)
If the Centurion has a 4 wire power cord: I will tie the chassis ground to the ground in the feed, the amp's bond to the feed's neutral and the 110V single phase lines to the amp's black/red. The ide
/archives//html/Amps/2003-12/msg00033.html (12,680 bytes)

8. Re: [Amps] 220V service for amplifier (score: 1)
Author: "Paul Christensen, Esq." <w9ac@arrl.net>
Date: Wed, 3 Dec 2003 09:10:12 -0500
"NEVER 'consider' or tie neutral to ground. They are NOT the same.... Neutral carries current by design, the ground should never carry current unless there is a fault." An excellent point Bill. All t
/archives//html/Amps/2003-12/msg00034.html (9,597 bytes)

9. RE: [Amps] 220V service for amplifier (score: 1)
Author: "Mike McCarthy, W1NR" <w1nr@eecorp.com>
Date: Wed, 3 Dec 2003 11:01:15 -0500
I agree with Bill. Most new installations require separate neutral and ground at the breaker box and for years, sub services had separate neutral and ground as well. Never consider neutral to be the
/archives//html/Amps/2003-12/msg00036.html (12,440 bytes)

10. Re: [Amps] 220V service for amplifier (score: 1)
Author: Gary Schafer <garyschafer@comcast.net>
Date: Wed, 03 Dec 2003 12:20:36 -0500
ka1xo@juno.com wrote: Dear Jason, On your amplifier there will more than likely be an attachment to the metal box where a grounding conductor can terminate. The metal frame of your amplifier should h
/archives//html/Amps/2003-12/msg00037.html (10,599 bytes)

11. Re: [Amps] 220V service for amplifier (score: 1)
Author: Ed Briggs <edbriggs@optonline.net>
Date: Wed, 03 Dec 2003 16:03:30 -0500
I appreciate the humor, but there have been sufficiently many tragic occurrences of the 'electrical equivalent' of this situation that there are now specific prohibitions in the NEC and local electri
/archives//html/Amps/2003-12/msg00039.html (14,351 bytes)

12. Re: [Amps] 220V service for amplifier (score: 1)
Author: "Michael Tope" <W4EF@dellroy.com>
Date: Wed, 3 Dec 2003 22:50:31 -0800
Jason, I ran into this problem with the Henry 2K-D that was donated to our local club station. Even when operated from a 240VAC circuit, the Henry still requires 120VAC from the mains to run the blow
/archives//html/Amps/2003-12/msg00041.html (11,813 bytes)

13. Re: [Amps] 220V service for amplifier (score: 1)
Author: R.Measures <r@somis.org>
Date: Wed, 3 Dec 2003 06:25:19 -0800
** For powering a single-phase amplifier with a capacitor-type HV filter, it is better to go with larger gauge wire than the electrical code specifies because I-peak is typically 10x I-average for c
/archives//html/Amps/2003-12/msg00043.html (11,763 bytes)

14. Re: [Amps] 220V service for amplifier (score: 1)
Author: R.Measures <r@somis.org>
Date: Wed, 3 Dec 2003 19:38:13 -0800
** What if the same tragic occurrence that severs the neutral wire also severs the ground wire? It seems to me that to assure against this possibility, two ground and two neutral wires are needed to
/archives//html/Amps/2003-12/msg00045.html (15,741 bytes)

15. Re: [Amps] 220V service for amplifier (score: 1)
Author: Ed Briggs <edbriggs@optonline.net>
Date: Thu, 04 Dec 2003 10:24:11 -0500
The Centurion is a 3 wire connection; 2 hot and the third is connected directly to the chassis and must be ground, not neutral. The Centurion does not use phase to ground to develop 120 v for the fan
/archives//html/Amps/2003-12/msg00047.html (14,747 bytes)

16. Re: [Amps] 220V service for amplifier (score: 1)
Author: "Ian White, G3SEK" <G3SEK@ifwtech.co.uk>
Date: Thu, 4 Dec 2003 08:00:11 +0000
R. Measures wrote: If you tie it to the neutral, there is a possibility of a voltage differentail between the amp chassis and the earth ground which can create a dangerous situation. ** But only if t
/archives//html/Amps/2003-12/msg00049.html (10,187 bytes)

17. Re: [Amps] 220V service for amplifier (score: 1)
Author: ka1xo@juno.com
Date: Thu, 4 Dec 2003 09:33:39 GMT
Dear Paul, I read your posting about the Alpha 77 series primary a.c. wiring shortcomings. My question is how does this affect taking my 77Sx into hotel rooms? Rich Measures already suggested using t
/archives//html/Amps/2003-12/msg00051.html (8,558 bytes)

18. RE: [Amps] 220V service for amplifier (score: 1)
Author: Joe Isabella <n3ji@yahoo.com>
Date: Thu, 4 Dec 2003 12:59:12 -0800 (PST)
Okay, okay, I misspoke. Sorry fellas!! My amplifier (and clothes dryer, for that matter) has only three wires -- two hots and a GROUND. I would assume that everyone knows that they are 180 out -- tha
/archives//html/Amps/2003-12/msg00053.html (15,199 bytes)

19. Re: [Amps] 220V service for amplifier (score: 1)
Author: W0UN -- John Brosnahan <shr@swtexas.net>
Date: Thu, 04 Dec 2003 05:58:00 -0600
While I was president of Alpha/Power and involved in repair of Alpha 77 amps I asked Dick Ehrhorn why he had designed the amps with only a 3-wire AC connection and with a 120 VAC blower since this de
/archives//html/Amps/2003-12/msg00057.html (12,457 bytes)

20. Re: [Amps] 220V service for amplifier (score: 1)
Author: Steven Grant W4IIV <stevengrant98@yahoo.com>
Date: Thu, 4 Dec 2003 05:59:27 -0800 (PST)
Most amps i have seen use the 3rd wire as a neutral.....If you have anything at all for power, you are gonna ground it anyways. the thread concerning the man who added the centurion that all of a sud
/archives//html/Amps/2003-12/msg00058.html (17,049 bytes)