Unfortunately, most residential buildings are nearly transparent to
lightning-induced currents
-- or any other kind of electrical activity.
Envision your home without any of the non-metallic materials. Since most
of us do not live in
an enclosed metal shell/screen (i.e., a Faraday shield), all the metallic bits
and pieces of the
building, plumbing, wiring, computers and radio equipment are simply hovering
in the space just
above the ground, as far as lightning and RF are concerned.
Our buildings keep the rain out and moderate the climate -- but do
essentially nothing to
protect us against electrical activities.
With this mental picture in mind, one can more easily grasped how exposed
our equipment and
wiring is to electric-magnetic fields of all kinds, including those produced by
nearby lightning.
Note that the bonding system must be low impedance at the frequency of the
currents in question.
As frequency goes up, this becomes more challenging to achieve -- which is
why wide copper
strapping is helpful and braid is must less helpful. Strap is used for its low
impedance, not for
its current carrying capacity, in this application. (Bus bar also has low
impedance, but is thick
because it is used for a different purpose: delivery of high-current at supply
voltages.) Lightning
radiates strong signals across a very wide part of the electro-magnetic
spectrum. (Notice how
'bright' a nearby bolt of lightning is way up in the visible light portion of
the spectrum. It has
similar 'brightness' or power all the way on down to DC.) A nearby strike will
induce currents
across a wide range of frequencies on the metal, wiring and electrical
equipment contained in that
nearly-invisible-to-RF house... and the strength of those currents at each
frequency can vary widely
depending on the impedance & resonance at each frequency.
The low-impedance earth bonding system helps in two respects:
a) keeps adjacent chassis floating at similar electrical potentials,
reducing the current flow
between the pieces of equpment.
b) provides a path to earth for most of the induced current which is of
lower impedance than
other, more damaging routes (e.g., via signal cabling).
(a) above also reduces the danger of electric shock to operators when a
fault occurs within a
piece of equipment for whatever reason, since fault current flowing into the
chassis will lift its
potential and that of the neighboring bonded equipment similarly. (Fault
current should be
short-lived if the protective systems [fuses, etc] have been properly designed.)
Note that no bonding system can keep equipment at the SAME potential to its
neighbors, to the
'entrance panel' (which is also floating in space), or to the earth. There is
always SOME
impedance, greater at higher frequencies, and therefore SOME potential
difference (voltage). A
well-designed and -implemented system will keep these impedances low and the
differences small
across a wide range of frequencies down to DC ... but it can never be zero.
As a result, the higher the current flow (induced or fault), the greater
the differences between
various bits of equipment and cabling. And, the higher the frequency of these
currents, the greater
the differences across distance -- i.e., the voltages at one physical spot will
difference from
those a few meters away. With sufficiently high induced or direct current, the
differences will be
too great and equipment damage will occur. With lower impedances across a
wider frequency range, an
installation will have a greater tolerance for these currents before damage
occurs. But every
installation will have a point at which damage can occur, so nothing is
'lightning proof'. We build
for a degree of lightning and fault tolerance to hopefully cover most events
(e.g., nearby strikes),
and accept that we will have to rebuild when overwhelmed by an extreme event.
(That's what
insurance is for.) Those in lightning-prone areas will have to invest more
heavily in better (and
more costly) techniques to reduce failures to an acceptably infrequent level,
or re-build more often.
Braid has much higher impedances than strap and, as Frank has pointed out,
its use should be
avoided whenever possible in the construction of an earthing system.
Sorry this was a bit long. I was in a rush and didn't take time to make it
brief.
73,
-- Eric K3NA
_______________________________________________
See: http://www.mscomputer.com for "Self Supporting Towers", "Wireless Weather
Stations", and lot's more. Call Toll Free, 1-800-333-9041 with any questions
and ask for Sherman, W2FLA.
_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk
|