My 3 wire drop comes from the telephone pole in my back yard, across my yard, 
to a metal pole on my house.  Through this metal 
pole
the 3 wires enter my house to my inside fuse panel.  Should I ground this 
outside metal pole to an outside earth ground rod, and 
connect
 it to my tower grounds ?

Confused,
Carl  K8AV



> It has nothing to do with tripping a breaker or not tripping a breaker
> because of multiple paths. The breaker is always in the hot lead.
> Whether the return path is via the neutral lead or the ground (green
> wire) lead or both, makes no difference to the breaker.
>
> The ground wire is connected to equipment chassis to ensure that there
> is a low resistance return path for a fault that may come in contact
> with the chassis. It also keeps that chassis close to earth potential in
> case of a fault so that fault path does not include a person in contact
> with that chassis and earth.
>
> The neutral and ground (green wire) are kept separate only so that
> neutral current does not flow on the ground wire under normal operation.
> If neutral current were to be allowed on the ground wire under normal
> operation it could raise the potential of a chassis above local ground
> due to voltage drop in the ground wire carrying current.
>
> By the way, there can be as many earth grounds of the grounding
> conductor as you may like. It doesn't have to be grounded to earth only
> at the panel. But the neutral must be grounded to earth only at the panel.
>
> 73
> Gary  K4FMX


_______________________________________________

See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless Weather 
Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with any questions 
and ask for Sherman, W2FLA.

_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>