> Subject: Re: [Amps] 4 wire 240VAC service? What to do now?
>
> On 4/4/2011 9:38 PM, Gary Schafer wrote:
> > Being that it is only 120 volts you have a hot, neutral and a ground
> wire
> > run out there. You should have the ground wire from the main panel
> connected
> > to the ground buss in the sub panel along with the local ground rod
> out
> > there. Do not bond the neutral to the sub panel ground.
>
> Ahhh, I thought if you had a ground rod and ground at the remote panel
> then the neutral was grounded at that point as well and that was the
> only condition under which the remote panel neutral was grounded. No
> ground rod at the remote panel and then neutral is not grounded there,
> but only back at the main panel.
>
> 73
>
> Roger (K8RI)
Under today's NEC rules you always need a ground rod at the remote panel if
the remote panel is not in the same building as the main panel. And they
want a separate ground and separate neutral wire run from the main panel.
Ground and neutral remain separate in the remote panel.
The only time that you do not need a ground rod at a remote location in
another building is if you only have one circuit out there as a light and
one outlet.
73
Gary K4FMX