Jeff,

I don't know of current Code that permits a circuit that lacks an equipment ground conductor run with the current-carrying conductors. That sort of thing was permitted in much older Codes, and old work is, for the most part, grandfathered. But it remains a really bad thing. To understand one reason why this is bad for ham radio (and component audio systems), see Slides 122-129 in this link, which are slides for a talk I did at Pacificon last fall and will do at Visalia next month. There's also a safety issue.

http://k9yc.com/GroundingAndAudio.pdf

73, Jim K9YC

On Mon,3/20/2017 2:36 PM, Jeff DePolo wrote:
Although a little different than the instant case, there are some situations
where NEC not only allows but requires that you to bond neutral to the
chassis of an appliance as a substitute for a separate EGC whre one doesn't
exist.  Electric dryers, ranges, and ovens come to mind.